Hello,

I'm thinking about getting a Generalc II power generator. I was wondering
if anyone had any experience either with the company or this specific
model. The Generac II model in question is EPS-8-AC, with transfer switch,
and the details are:

Controls:

Mode Switch, Auto Switch Utility failure / 7 day exerciser, Off Switch
Stops unit. Power is removed. Control and charger still operate.

Manual/Test (start) Start with starter control, unit stays on. If utility
fails, transfer to load takes place. Engine Start Sequence Cyclic ranking:
     7 seconds on, 7 seconds rest (90 sec. maximum duration)
     Engine Warm-up 10 seconds
     Engine Cool-Down 1 minute
     Starter Lockout Starter cannot re-engage until 5 sec. after engine
     has stopped
     2 Amp Timed Trickle Battery Charger Standard
     Automatic Low Oil Pressure Shutdown Standard
     Overspeed Shutdown Standard, 70 Hz
     High Temperature Shutdown Standard
     Overcrank Protection Standard
     Safety Fuse Standard

Model                            EPS-8-AC
Rated Power (KW)*                8
Voltage** 60Hz                   120/240V, 1�
Amps @ 120/240V, 1� 60Hz         66.6/33.3
Engine/Alternator RPM            3600
Engine                           570CC
                                 OHVI V-TWIN
Fuel                             GASEOUS
Fuel Consumption/Full Load
    Natural Gas - cu ft/hr        45
    Propane - cu ft/hr (gal/hr)   67 (1.8)
Engine Cooling                    AIR

Any comments or suggestions?

danielle

---------: Danielle Bercel :-----------: dbercel@hpcc01.corp.hp.com -]
:Stupidity got me into this mess, why     : 1501 Page Mill Rd, 6U W62   :
:can't it get me out?                     : Palo Alto, CA. 94304        :
:                                         : (415) 857-6512              :

-------------------==== Posted via Deja News ====-----------------------
      http://www.dejanews.com/     Search, Read, Post to Usenet
Re: Generac II Generator
#1557
Author: glena
Date: Fri, 04 Jul 1997 00:00
62 lines
3013 bytes
In article <867987640.7956@dejanews.com>, dbercel@corp.hp.com writes:
> 
> I'm thinking about getting a Generalc II power generator. I was wondering
> if anyone had any experience either with the company or this specific
> model. The Generac II model in question is EPS-8-AC, with transfer switch,
> and the details are:

hummm ..... in one sense, it kinda sounds like overkill.  I'm refering
to all of the auto switching.  In another sense, Generac tends to be
good as a boat anchor.  The warranty tends to really suck.  Especially
if they use a Briggs & Stratton engine.  The B&S warranty covers only
defects in materials and workmanship.  Funny thing is that when you take
it in to have it repaired on warranty, all of the problems are due to
"normal wear and tear".  Read that as meaning "not covered".

Running on propane might be a really good idea, considering that the use
is only occasional.  This would prevent the varnish buildup that would
tend to occur with gasoline engines. 

>      Starter Lockout Starter cannot re-engage until 5 sec. after engine
>      has stopped

Why?

>      2 Amp Timed Trickle Battery Charger Standard

Awfully low.  All of the low end Hondas have 8 Amp as standard. 

>      Automatic Low Oil Pressure Shutdown Standard

This is pretty standard on most generators, today.

>      Overspeed Shutdown Standard, 70 Hz

Hummm....interesting.  So if the governor doesn't work, for some reason,
it may run too fast.  If this happens, it shuts off?

>      High Temperature Shutdown Standard

This sounds like a good idea.

>      Safety Fuse Standard

Again, pretty standard.  I don't remember seeing *any* generator without
a circuit breaker or fuse on the output.

Now, I don't remember, but I *think* that Honda has propane conversions
available on some models.

Additionally, when you get up into the 8kW area, they tend to be water
cooled (quieter, longer life).

If you haven't checked out Honda, I would suggest that you do.  Remember,
though:  Do *not* pay list.  Hint:  My 2400 listed for $1300.  It was on
"sale" for about $950.  I ended up paying $800 -- including the 4 year
extended warranty (don't bother -- you don't need it).
--
Do not underestimate your abilities.  That is your boss's job.
It is your job to find ways around your boss's roadblocks.
_______________________________________________________________
Glen Appleby  glena@mail.cruzio.com  http://www2.cruzio.com/~glena/
Re: Generac II Generator
#1558
Author: Danielle Bercel
Date: Fri, 04 Jul 1997 00:00
16 lines
959 bytes
Glen,

Thanks for the advice. Generac also makes a liquid colled 8K model and
I'll check into that.

danielle (with all the wood) bercel

[-----------: Danielle Bercel :-----------: dbercel@hpcc01.corp.hp.com
-]
:If you're not living on the edge you are : 1501 Page Mill Rd, 6U W62  
:
:taking up too much space.                : Palo Alto, CA. 94304       
:
:                                         : (415) 857-6512             
:
Re: Generac II Generator
#1559
Author: phtp
Date: Sat, 05 Jul 1997 00:00
14 lines
1067 bytes
In article <33BD7F4D.3502@corp.hp.com>, Danielle Bercel <dbercel@corp.hp.com> writes:
> Glen,
> 
> Thanks for the advice. Generac also makes a liquid colled 8K model and
> I'll check into that.
> 
Any idea what brand the engine is?  Onan, perhaps?
pH

  
* D. Pureheart Steinbruner              Proud Morris Minor Owner since  *  
* KD6 CYC  phtp@bbs.cruzio.com          1973. (Hey!  Stop laughing!)    *
* Aptos, California                     Yes, it still runs.             *