Over-taxing service entrance panel?
Author: DaveC
Date: Thu, 07 Feb 2002 15:58
Date: Thu, 07 Feb 2002 15:58
13 lines
1703 bytes
1703 bytes
Practically speaking, how can one tell when one is drawing too much power from the service panel? I've got an old Zinsco brand box from the 50's, and while I know it should be upgraded, and eventually will, I'd like to know that the additional breaker I am adding is going on the correct phase, the one that is currently drawing the least. Is simple mathematics (adding up the loads on each circuit/phase) the best way? Measurements? Thanks, Dave (in the USA)
Re: Over-taxing service entrance panel?
Author: Zoran Matic
Date: Thu, 07 Feb 2002 19:17
Date: Thu, 07 Feb 2002 19:17
58 lines
3390 bytes
3390 bytes
If I udnerstood you corectly you want to add a single phase recept (or a group in the same circuit) but you don't know on which phase is best to connect it . If so I can tell you the way of household el. inst. designing considering load distribution. (At least el. engeneers common way in Serbia). Draw a table with 3 rows (representing phases R,S,T) and with as many columnes as the number of circuits in the old panell is(each column represents one single or three phase circuit) . Than add one extra column for the new circuit. Now write the circuit loads into apropriate cels (for 3 phase circuit every one of 3 cels in column should contain 1/3 of total 3 phase load). Calculate total sums of loads for each phase and find out which one is sutable to use. We rate household single phase socket load 2.5 kW and 3 phase to 5.5 You should easily find out the data for other recepts. To determine witch recepts are conected to witch phase pull out main breakers (one at the time) and see what recepts are disconected (use probe or wired bulbs or voltmeter to indicate voltage loss). You may connect a new circuit even at overloaded phase (considering table) if you now that most powerful recepts that are conected on that phase will not be used at the same time. Analitical method is more suitable then measuremant and it is common eng. practice in YU. Regards, Zoran Matic, contructins el. installatins eng. DaveC <anon@me.invalid> wrote in message news:01HW.B887E41C0045E4921AEDF5D8@news.dnai.com... > Practically speaking, how can one tell when one is drawing too much power > from the service panel? > > I've got an old Zinsco brand box from the 50's, and while I know it should be > upgraded, and eventually will, I'd like to know that the additional breaker I > am adding is going on the correct phase, the one that is currently drawing > the least. > > Is simple mathematics (adding up the loads on each circuit/phase) the best > way? Measurements? > > Thanks, > Dave (in the USA) >
Re: Over-taxing service entrance panel?
Author: Phil Allison
Date: Thu, 07 Feb 2002 20:23
Date: Thu, 07 Feb 2002 20:23
5 lines
1470 bytes
1470 bytes
How about over-taxing news groups with persistant cross posting from Dave
C?
Phil
Re: Over-taxing service entrance panel?
Author: DaveC
Date: Fri, 08 Feb 2002 08:02
Date: Fri, 08 Feb 2002 08:02
11 lines
1650 bytes
1650 bytes
On Thu, 7 Feb 2002 12:23:49 -0800, Phil Allison wrote (in message <_fB88.1782$BE4.5768@newsfeeds.bigpond.com>): > > How about over-taxing news groups with persistant cross posting from DaveC? Well, Phil, I said it before and I'll say it again: Cross-posting isn't illegal. *Inappropriate* cross-posting should be. All ng's posted to are appropriate to this subject. D.
Re: Over-taxing service entrance panel?
Author: DaveC
Date: Fri, 08 Feb 2002 08:03
Date: Fri, 08 Feb 2002 08:03
44 lines
2937 bytes
2937 bytes
On Thu, 7 Feb 2002 11:17:24 -0800, Zoran Matic wrote (in message <a3uk4q$39t$1@news.eunet.yu>): > If I udnerstood you corectly you want to add a single phase recept (or a > group in the same circuit) but you don't know on which phase is best to > connect it . > > If so I can tell you the way of household el. inst. designing considering > load distribution. (At least el. engeneers common way in Serbia). > > Draw a table with 3 rows (representing phases R,S,T) and with as many > columnes as the number of circuits in the old panell is(each column > represents one single or three phase circuit) . Than add one extra column > for the new circuit. > > Now write the circuit loads into apropriate cels (for 3 phase circuit every > one of 3 cels in column should contain 1/3 of total 3 phase load). > > Calculate total sums of loads for each phase and find out which one is > sutable to use. > > We rate household single phase socket load 2.5 kW and 3 phase to 5.5 > > You should easily find out the data for other recepts. > > To determine witch recepts are conected to witch phase pull out main > breakers (one at the time) and see what recepts are disconected (use probe > or wired bulbs or voltmeter to indicate voltage loss). > > You may connect a new circuit even at overloaded phase (considering table) > if you now that most powerful recepts that are conected on that phase will > not be used at the same time. > > > Analitical method is more suitable then measuremant and it is common eng. > practice in YU. > > Regards, > Zoran Matic, > contructins el. installatins eng. Thanks, Zoran. Analytical approach it is! Dave
Re: Over-taxing service entrance panel?
Author: Rod Speed
Date: Fri, 08 Feb 2002 08:55
Date: Fri, 08 Feb 2002 08:55
13 lines
2071 bytes
2071 bytes
DaveC <anon@me.invalid> wrote in message news:01HW.B888C604000799161B345AF8@news.dnai.com... > Phil Allison wrote >>> How about over-taxing news groups with persistant cross posting from DaveC? > Well, Phil, I said it before and I'll say it again: Cross-posting > isn't illegal. *Inappropriate* cross-posting should be. > > All ng's posted to are appropriate to this subject. aus.electronics isnt really, the mains system is rather different.
Re: Over-taxing service entrance panel?
Author: Phil Allison
Date: Fri, 08 Feb 2002 11:00
Date: Fri, 08 Feb 2002 11:00
18 lines
2002 bytes
2002 bytes
"DaveC" <anon@me.invalid> wrote in message
news:01HW.B888C604000799161B345AF8@news.dnai.com...
> > > How about over-taxing news groups with persistant cross posting from
DaveC?
>
> Well, Phil, I said it before and I'll say it again: Cross-posting isn't
> illegal. *Inappropriate* cross-posting should be.
>
> All ng's posted to are appropriate to this subject.
** Dave, you are a revolting little turd. You could easily post your
stupid trolls separately but you are too damn lazy to do so. Fuck you.
Phil.
Re: Over-taxing service entrance panel?
Author: DaveC
Date: Fri, 08 Feb 2002 15:52
Date: Fri, 08 Feb 2002 15:52
13 lines
1835 bytes
1835 bytes
> aus.electronics isnt really, the mains system is rather different. I'd gotten some rather bright replies to previous posts on the subject of power mains from this ng. If you've got another ng you'd recommend for the topic of power, please suggest. > Do what I do and block anything from him using "Block Sender" in Outlook If you wish. The simplest solution. "If you don't want to read it, don't." Dave
Re: Over-taxing service entrance panel?
Author: DaveC
Date: Fri, 08 Feb 2002 15:54
Date: Fri, 08 Feb 2002 15:54
8 lines
1588 bytes
1588 bytes
On Fri, 8 Feb 2002 3:19:47 -0800, Milesnz wrote (in message <6vO88.9171$Lv.1096024@news.xtra.co.nz>): > Do what I do and block anything from him using "Block Sender" in Outlook As I do with Phil's posts. Dave
Re: Over-taxing service entrance panel?
Author: Rod Speed
Date: Fri, 08 Feb 2002 23:09
Date: Fri, 08 Feb 2002 23:09
23 lines
2770 bytes
2770 bytes
DaveC <anon@me.invalid> wrote in message news:01HW.B889344A000C6C7D1B3551E8@news.dnai.com... > Rod Speed wrote >> DaveC <anon@me.invalid> wrote in message >>> All ng's posted to are appropriate to this subject. >> aus.electronics isnt really, the mains system is rather different. > I'd gotten some rather bright replies to previous > posts on the subject of power mains from this ng. Yeah, fair point. > If you've got another ng you'd recommend for the topic of power, please suggest. Nar, its one of those areas that doesnt have a specific group that I am aware of. To get back to your original question, in this country the capacity of the main entrance panel is essentially determined by the cabling used to connect it to the service mains. And thats almost entirely the number of phases and the conductor used. But our system is quite different on the phase detail to yours.
Re: Over-taxing service entrance panel?
Author: Rod Speed
Date: Fri, 08 Feb 2002 23:15
Date: Fri, 08 Feb 2002 23:15
21 lines
2542 bytes
2542 bytes
Phil Allison <bilup@bigpond.com> wrote in message news:I5O88.2222$BE4.7549@newsfeeds.bigpond.com... > DaveC <anon@me.invalid> wrote >>>> How about over-taxing news groups with persistant cross posting from DaveC? >> Well, Phil, I said it before and I'll say it again: Cross-posting >> isn't illegal. *Inappropriate* cross-posting should be. >> All ng's posted to are appropriate to this subject. > Dave, you are a revolting little turd. You could easily post your > stupid trolls separately but you are too damn lazy to do so. Fuck you. Wota fucking wanker. Only a fool demands that they be separately posted instead of crossposted. Any decent newsreader automatically marks all copys as read when the first copy is read with a crossposted post. Much better than having to mark each one as read in all the groups that it appears in, stupid.
Re: Over-taxing service entrance panel?
Author: Herb Stein
Date: Sat, 09 Feb 2002 02:48
Date: Sat, 09 Feb 2002 02:48
63 lines
3874 bytes
3874 bytes
"DaveC" <anon@me.invalid> wrote in message news:01HW.B888C6390007A5921B345AF8@news.dnai.com... > On Thu, 7 Feb 2002 11:17:24 -0800, Zoran Matic wrote > (in message <a3uk4q$39t$1@news.eunet.yu>): > > > If I udnerstood you corectly you want to add a single phase recept (or a > > group in the same circuit) but you don't know on which phase is best to > > connect it . > > > > If so I can tell you the way of household el. inst. designing considering > > load distribution. (At least el. engeneers common way in Serbia). > > > > Draw a table with 3 rows (representing phases R,S,T) and with as many > > columnes as the number of circuits in the old panell is(each column > > represents one single or three phase circuit) . Than add one extra column > > for the new circuit. > > > > Now write the circuit loads into apropriate cels (for 3 phase circuit every > > one of 3 cels in column should contain 1/3 of total 3 phase load). > > > > Calculate total sums of loads for each phase and find out which one is > > sutable to use. > > > > We rate household single phase socket load 2.5 kW and 3 phase to 5.5 > > > > You should easily find out the data for other recepts. > > > > To determine witch recepts are conected to witch phase pull out main > > breakers (one at the time) and see what recepts are disconected (use probe > > or wired bulbs or voltmeter to indicate voltage loss). > > > > You may connect a new circuit even at overloaded phase (considering table) > > if you now that most powerful recepts that are conected on that phase will > > not be used at the same time. > > > > > > Analitical method is more suitable then measuremant and it is common eng. > > practice in YU. > > > > Regards, > > Zoran Matic, > > contructins el. installatins eng. > > Thanks, Zoran. Analytical approach it is! > > Dave There is nothing to analyze. Pu it a 20 amp breaker with 12 gauge out of it and it will handle it. Get a grip. -- Herb Stein The Herb Stein Group www.herbstein.com herb@herbstein.com 314 952-4601