10T and number of twists per foot.
#1015
Author: Steven Lendt
Date: Thu, 21 Jan 1993 21:37
14 lines
1332 bytes
How many twists per foot in solid core unshelded twisted pair wire are
needed to make it live up to level 3 10baseT spec?
Also, how many punch blocks (old 66 type) is it safe to go through if the 
total wire length is not greater than 75 meters?

Thanks in advance!
 ____________________________________________________________________________
|  Steven Lendt, Campus Network Mgr   |   Internet: slendt@unocdc.unomaha.edu|
|  University of Nebraska at Omaha    |   Bitnet (via gateway):              |
|  Computing and Data Communications  |     slendt%unocdc.unomaha.edu@unlvax1|
|  6001 Dodge Street                  |   Voice Phone (402) 554-2523         |
|  Omaha, NE 68182-0051 USA           |   Fax (402) 554-3475                 |
|  The attention span of a computer is only as long as its electrical cord.  |
 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Re: 10T and number of twists per foot.
#1037
Author: Dan Pike
Date: Sun, 24 Jan 1993 22:45
15 lines
1225 bytes
In article <slendt.105.727652267@unomaha.edu> Steven Lendt,
slendt@unomaha.edu writes:
>How many twists per foot in solid core unshelded twisted pair wire are
>needed to make it live up to level 3 10baseT spec?
>Also, how many punch blocks (old 66 type) is it safe to go through if
the 
>total wire length is not greater than 75 meters?

I'm pretty sure the recommended number of twists per foot is 7tpf.  As
far as the punch block question goes, when I was working at Apple we
figured out that each punch on a 66 block added the equivalent of about
20 feet of cabling.  This wasn't any scientific testing though.  I think
we measured it with a TDR.

-Dan
Re: 10T and number of twists per foot.
#1068
Author: tanemeth
Date: Wed, 27 Jan 1993 23:40
16 lines
1287 bytes
In article <slendt.105.727652267@unomaha.edu>, slendt@unomaha.edu (Steven Lendt) writes:
> How many twists per foot in solid core unshelded twisted pair wire are
> needed to make it live up to level 3 10baseT spec?

EIA568 spec. says "7 to 10 twists per foot".  Most cables I have seen interpret
this as 7 for pair 1 (blue), 8 for pair 2 (orange), 9 for pair 3 (green) and
10 for pair 4 (brown).

> Also, how many punch blocks (old 66 type) is it safe to go through if the
> total wire length is not greater than 75 meters?

Always as FEW AS POSSIBLE.  Should ideally be 3 max.  From memory, you need to
deduct 2m from max usable length for each extra cross-connect.


Tom Nemeth