Two phases to house - loss of neutral
Author: Sylvia Else
Date: Tue, 24 Nov 2009 00:10
Date: Tue, 24 Nov 2009 00:10
16 lines
1705 bytes
1705 bytes
I have to phases of power supply to my house - so three power lines, two phases plus neutral. I've on occasion wondered what would happen if we lost the neutral line. It seems to me that we'd then have the voltage between the two phases across two sets of appliances, one set attached to one phase, and the other set attached to the other phase, with the two sets in series as a result of their common connection to the neutral wire. Since the two sets are unlikely to represent equal loads, the net result would be a large overvoltage on one set of appliances. My electrician says it's not an issue, but I can't see why. Any thoughts? Sylvia.
Re: Two phases to house - loss of neutral
Author: kreed
Date: Tue, 24 Nov 2009 00:57
Date: Tue, 24 Nov 2009 00:57
72 lines
4327 bytes
4327 bytes
On Nov 24, 10:10 am, Sylvia Else <syl...@not.at.this.address> wrote: > I have to phases of power supply to my house - so three power lines, two > phases plus neutral. > > I've on occasion wondered what would happen if we lost the neutral line. > It seems to me that we'd then have the voltage between the two phases > across two sets of appliances, one set attached to one phase, and the > other set attached to the other phase, with the two sets in series as a > result of their common connection to the neutral wire. Since the two > sets are unlikely to represent equal loads, the net result would be a > large overvoltage on one set of appliances. > > My electrician says it's not an issue, but I can't see why. > > Any thoughts? > > Sylvia. You are both right and wrong as in the absence of Neutral line, a lot of the neutral current (imbalance) would probably flow via your earth stake back to the transformer neutral or to a neighbours neutral via their earth stake and while its not a perfect situation, imbalance probably would not be as bad as you might think ? Of course, if there is a long run through earth (terra firma) back to the nearest neutral, the soil is really dry, the earth stake is sub- standard etc etc it might not work very well. Years and years back I once saw the result of this at a 3 phase installation at a carnival, we were called out to fix They would have with them, and take from site to site portable fuse boxes with a 3 phase plug, going to a box with breakers feeding rows of power points going to each phase (like in a normal building installation, but portable). They would plug in all their gear to these sockets, and plug the 3 phase into the 3 phase sockets provided at the venues. Of course, a lot of the carnival workers would probably just plug things in at random, and who knows what load would be on the end of each lead. There could also be very large numbers of flashing lights on one lead too, so the load would be less than perfect, and surely not anywhere near balanced or stable ;) One case, the neutral lead broke off. On one phase there was a lot of damage to computer gear / arcade games (same sort of thing - switchmode power supplies) etc. Some was just blown fuses, some worse. Note, they didn't have the earth and neutral bonded inside the box, and didn't have a separate earth stake, where in a home fuse box they would. 2 phase situation like yours would be a similar result, unless the load was really well balanced, and consisting of mostly NON-switchmode power supply type devices. The phase with the lowest load would suffer overvoltage. This load imbalance and voltage difference would change all the time as various appliances automatically switch off and on, like fridges, air cons, electric HWS etc. Light bulbs may blow from overvoltage, this would also change the balance Try connecting 12v bulbs of different wattages in series across 24v and see what happens. The voltage will not be the same across each. Much the same thing.
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 00:58
Date: Tue, 24 Nov 2009 00:58
56 lines
3280 bytes
3280 bytes
"Stupider than Anyone Else" >I have to phases of power supply to my house - so three power lines, two >phases plus neutral. > > I've on occasion wondered what would happen if we lost the neutral line. > It seems to me that we'd then have the voltage between the two phases > across two sets of appliances, one set attached to one phase, and the > other set attached to the other phase, with the two sets in series as a > result of their common connection to the neutral wire. Since the two sets > are unlikely to represent equal loads, the net result would be a large > overvoltage on one set of appliances. > > My electrician says it's not an issue, but I can't see why. ** Loss of the neutral conductor in a 3 phase ( or 2 phase) AC supply system can easily be a DISASTROUS event. For example: In the live entertainment productions - high powered lighting and sound systems operate from 3 phase outlets via a hefty 5 pin plug and socket. If, due to wear and tear or damage to the plug or socket, one of the phases drops out - that is an annoyance but not a disaster. However, if the pin carrying the neutral fails to connect or as is often the case *disconnects* during a show because of overheating - ALL HELL BREAKS LOOSE !! Typically, some of the lamps will glow very brightly for a second or two and fail, then other previously dim lamps will follow suit. The AC fuses in amplifiers will pop instantly and some equipment will be seriously damaged when the PSU sections are destroyed. It all happens in a few seconds, while the operators stand there with their mouths open !!! The MEN system: In Australia, AC power delivery uses a system called " Multiple Earth Neutral " - which requires that the neutral conductors in a premises be connected to the plumbing system at the distribution board (ie power box). It also requires that an earth stake be installed for the same purpose, but some older premises may not have this. Because EVERY premises has MEN installed, the ground itself and underground metal plumbing act as an alternative neutral, should the supply conductor feeding a given premises fail. The disastrous event sometimes experienced in live entertainment systems is hardly possible in domestic or commercial premises. So the sparky is right. .... Phil
Re: Two phases to house - loss of neutral
Author: Trevor Wilson
Date: Tue, 24 Nov 2009 02:15
Date: Tue, 24 Nov 2009 02:15
26 lines
1878 bytes
1878 bytes
Sylvia Else wrote: > I have to phases of power supply to my house - so three power lines, > two phases plus neutral. > > I've on occasion wondered what would happen if we lost the neutral > line. It seems to me that we'd then have the voltage between the two > phases across two sets of appliances, one set attached to one phase, > and the other set attached to the other phase, with the two sets in > series as a result of their common connection to the neutral wire. > Since the two sets are unlikely to represent equal loads, the net > result would be a large overvoltage on one set of appliances. > > My electrician says it's not an issue, but I can't see why. > > Any thoughts? **Not an issue, due to the MEN system used in AUSTRALIA. Cross-posting to an international group will guarantee a bunch of useless comments. Pay attention to Australian posters only. Your electrician is correct. -- Trevor Wilson www.rageaudio.com.au
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Tue, 24 Nov 2009 02:16
Date: Tue, 24 Nov 2009 02:16
29 lines
2324 bytes
2324 bytes
Phil Allison wrote: > "Dave Platt" >> Sylvia Else >> >>> I have to phases of power supply to my house - so three power lines, two >>> phases plus neutral. >>> >>> I've on occasion wondered what would happen if we lost the neutral line. >>> It seems to me that we'd then have the voltage between the two phases >>> across two sets of appliances, one set attached to one phase, and the >>> other set attached to the other phase, with the two sets in series as a >>> result of their common connection to the neutral wire. Since the two >>> sets are unlikely to represent equal loads, the net result would be a >>> large overvoltage on one set of appliances. >>> >>> My electrician says it's not an issue, but I can't see why. >> It's a huge issue. > > > ** Sylvia lives in Sydney, Australia and is a MASSIVE TROLL. > > Nuts of her the post such a COUNTRY SPECIFIC message to a US newsgroup. Last time I checked, multiphase power supply was pretty universal, and the principles to be applied in understanding the consequences of faults would be the same. Or perhaps you want to argue that the different voltage in Australia is the deciding factor. Sylvia.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Tue, 24 Nov 2009 02:18
Date: Tue, 24 Nov 2009 02:18
29 lines
2176 bytes
2176 bytes
Trevor Wilson wrote: > Sylvia Else wrote: >> I have to phases of power supply to my house - so three power lines, >> two phases plus neutral. >> >> I've on occasion wondered what would happen if we lost the neutral >> line. It seems to me that we'd then have the voltage between the two >> phases across two sets of appliances, one set attached to one phase, >> and the other set attached to the other phase, with the two sets in >> series as a result of their common connection to the neutral wire. >> Since the two sets are unlikely to represent equal loads, the net >> result would be a large overvoltage on one set of appliances. >> >> My electrician says it's not an issue, but I can't see why. >> >> Any thoughts? > > **Not an issue, due to the MEN system used in AUSTRALIA. Cross-posting to an > international group will guarantee a bunch of useless comments. Pay > attention to Australian posters only. > > Your electrician is correct. > > From the replies, the same system applies in the US. But people have still had problems. Sylvia.
Re: Two phases to house - loss of neutral
Author: Trevor Wilson
Date: Tue, 24 Nov 2009 02:22
Date: Tue, 24 Nov 2009 02:22
35 lines
2216 bytes
2216 bytes
Sylvia Else wrote: > Trevor Wilson wrote: >> Sylvia Else wrote: >>> I have to phases of power supply to my house - so three power lines, >>> two phases plus neutral. >>> >>> I've on occasion wondered what would happen if we lost the neutral >>> line. It seems to me that we'd then have the voltage between the two >>> phases across two sets of appliances, one set attached to one phase, >>> and the other set attached to the other phase, with the two sets in >>> series as a result of their common connection to the neutral wire. >>> Since the two sets are unlikely to represent equal loads, the net >>> result would be a large overvoltage on one set of appliances. >>> >>> My electrician says it's not an issue, but I can't see why. >>> >>> Any thoughts? >> >> **Not an issue, due to the MEN system used in AUSTRALIA. >> Cross-posting to an international group will guarantee a bunch of >> useless comments. Pay attention to Australian posters only. >> >> Your electrician is correct. >> >> > > From the replies, the same system applies in the US. But people have > still had problems. **AFAIK, the US system is fundamentally different to ours. -- Trevor Wilson www.rageaudio.com.au
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 02:25
Date: Tue, 24 Nov 2009 02:25
24 lines
1571 bytes
1571 bytes
"Stupider than Anyone Else Alive " > >> ** Sylvia lives in Sydney, Australia and is a MASSIVE TROLL. >> >> Nuts of her the post such a COUNTRY SPECIFIC message to a US newsgroup. > > Last time I checked, multiphase power supply was pretty universal, and the > principles to be applied in understanding the consequences of faults would > be the same. ** 100 % WRONG !!! The question this insane bitch posted IS country SPECIFIC !!! Cos it was about her house in * Sydney, Australia *. See Trevor Wilson's reply. .... Phil
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 02:31
Date: Tue, 24 Nov 2009 02:31
28 lines
1613 bytes
1613 bytes
"Stupider than Anyone Else on Earth " > > Trevor Wilson wrote: >> >> My electrician says it's not an issue, but I can't see why. >>> >>> Any thoughts? >> >> **Not an issue, due to the MEN system used in AUSTRALIA. Cross-posting to >> an international group will guarantee a bunch of useless comments. Pay >> attention to Australian posters only. >> >> Your electrician is correct. >> > > From the replies, the same system applies in the US. ** Wot INSANE FUCKING CRAPOLOGY !! The only relevant reply from the US so far indicates the DIRECT OPPOSITE . Piss off - TROLLING BITCH. ..... Phil
Re: Two phases to house - loss of neutral
Author: kreed
Date: Tue, 24 Nov 2009 02:33
Date: Tue, 24 Nov 2009 02:33
44 lines
3277 bytes
3277 bytes
On Nov 24, 12:16 pm, Sylvia Else <syl...@not.at.this.address> wrote: > Phil Allison wrote: > > "Dave Platt" > >> Sylvia Else > > >>> I have to phases of power supply to my house - so three power lines, two > >>> phases plus neutral. > > >>> I've on occasion wondered what would happen if we lost the neutral line. > >>> It seems to me that we'd then have the voltage between the two phases > >>> across two sets of appliances, one set attached to one phase, and the > >>> other set attached to the other phase, with the two sets in series as a > >>> result of their common connection to the neutral wire. Since the two > >>> sets are unlikely to represent equal loads, the net result would be a > >>> large overvoltage on one set of appliances. > > >>> My electrician says it's not an issue, but I can't see why. > >> It's a huge issue. > > > ** Sylvia lives in Sydney, Australia and is a MASSIVE TROLL. > > > Nuts of her the post such a COUNTRY SPECIFIC message to a US newsgroup. > > Last time I checked, multiphase power supply was pretty universal, and > the principles to be applied in understanding the consequences of faults > would be the same. Or perhaps you want to argue that the different > voltage in Australia is the deciding factor. > > Sylvia. From what I can gather, pretty much every home in the US has a 120v - 0 - 120v system where the 2x 120v's are 180 degrees out of phase. Between the 2 phases 240v is available for stoves, air conditioners etc. In Australia, most separate homes have a straight single phase 240v supply, its not common for there to be 2,3 separate phases to the average house. Therefore the scenario Sylvia mentions is less likely to occur, as not many people have this multi phase system. The exception here could be blocks of flats, if the main neutral to the building fails, and there isn't a good earth, the imbalance could be a risk.
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 02:36
Date: Tue, 24 Nov 2009 02:36
20 lines
1418 bytes
1418 bytes
"Trevor Wilson" > > **AFAIK, the US system is fundamentally different to ours. ** In the US and Canada - it is NOT permitted to link neutral and earth or plumbing within a premises. See here under the heading "Regulations". http://en.wikipedia.org/wiki/Earthing_system The MEN system used here in Australia seems to be unique. See last para on same page. ..... Phil
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 02:40
Date: Tue, 24 Nov 2009 02:40
23 lines
1905 bytes
1905 bytes
"kreed" > From what I can gather, pretty much every home in the US has a 120v - > 0 - 120v system where the 2x 120v's are 180 degrees out of phase. > Between the 2 phases 240v is available for stoves, air conditioners > etc. > > In Australia, most separate homes have a straight single phase 240v > supply, its not common for there to be 2,3 separate phases to the > average house. Therefore the scenario Sylvia mentions is less likely > to occur, as not many people have this multi phase system. > > The exception here could be blocks of flats, if the main neutral to > the building fails, and there isn't a good earth, the imbalance could > be a risk. ** There is always a good "earth" available - courtesy of the water mains in the street being linked to neutral at every premises. ..... Phil
Re: Two phases to house - loss of neutral
Author: kreed
Date: Tue, 24 Nov 2009 02:47
Date: Tue, 24 Nov 2009 02:47
72 lines
4557 bytes
4557 bytes
On Nov 24, 10:58 am, "Phil Allison" <phi...@tpg.com.au> wrote: > "Stupider than Anyone Else" > > >I have to phases of power supply to my house - so three power lines, two > >phases plus neutral. > > > I've on occasion wondered what would happen if we lost the neutral line. > > It seems to me that we'd then have the voltage between the two phases > > across two sets of appliances, one set attached to one phase, and the > > other set attached to the other phase, with the two sets in series as a > > result of their common connection to the neutral wire. Since the two sets > > are unlikely to represent equal loads, the net result would be a large > > overvoltage on one set of appliances. > > > My electrician says it's not an issue, but I can't see why. > > ** Loss of the neutral conductor in a 3 phase ( or 2 phase) AC supply system > can easily be a DISASTROUS event. > > For example: > > In the live entertainment productions - high powered lighting and sound > systems operate from 3 phase outlets via a hefty 5 pin plug and socket. If, > due to wear and tear or damage to the plug or socket, one of the phases > drops out - that is an annoyance but not a disaster. > > However, if the pin carrying the neutral fails to connect or as is often the > case *disconnects* during a show because of overheating - ALL HELL > BREAKS LOOSE !! > > Typically, some of the lamps will glow very brightly for a second or two and > fail, then other previously dim lamps will follow suit. The AC fuses in > amplifiers will pop instantly and some equipment will be seriously damaged > when the PSU sections are destroyed. It all happens in a few seconds, while > the operators stand there with their mouths open !!! > > The MEN system: > > In Australia, AC power delivery uses a system called " Multiple Earth > Neutral " - which requires that the neutral conductors in a premises be > connected to the plumbing system at the distribution board (ie power box). > It also requires that an earth stake be installed for the same purpose, but > some older premises may not have this. > > Because EVERY premises has MEN installed, the ground itself and underground > metal plumbing act as an alternative neutral, should the supply conductor > feeding a given premises fail. The disastrous event sometimes experienced in > live entertainment systems is hardly possible in domestic or commercial > premises. > > So the sparky is right. > The scenario you mention with live entertainment is particularly bad, as when you think about it, unlike a fixed installation you can't bond the earth and neutral in these portable 3 phase to 240v outlet mains boxes. If you did, it would trip any earth leakage breakers upstream - if these are fitted. To make matters worse, in live entertainment, the major loads are almost all amplifiers, and lighting. None of these are stable loads (amplifiers are changing their load current draw constantly with the music and lights are being dimmed, flashed often in large groups. ) Therefore if the neutral lead fails, there is no bonding to earth to back it up, unlike a residence, and with the inherent instabilty of the load balance , massive damage is guaranteed. > .... Phil
Re: Two phases to house - loss of neutral
Author: Trevor Wilson
Date: Tue, 24 Nov 2009 03:20
Date: Tue, 24 Nov 2009 03:20
27 lines
1811 bytes
1811 bytes
Phil Allison wrote: > "Trevor Wilson" > >> >> **AFAIK, the US system is fundamentally different to ours. > > > ** In the US and Canada - it is NOT permitted to link neutral > and earth or plumbing within a premises. > > See here under the heading "Regulations". > > http://en.wikipedia.org/wiki/Earthing_system > > The MEN system used here in Australia seems to be unique. > > See last para on same page. **Interesting. I'd have thunk that some places in Europe might employ a similar system. Guess not. Ever since I ran across my first US audio product with a high value resistor to chassis from (allegedly) Neutral, I realised that the US system was highly flawed. -- Trevor Wilson www.rageaudio.com.au
Re: Two phases to house - loss of neutral
Author: Bob AZ
Date: Tue, 24 Nov 2009 03:24
Date: Tue, 24 Nov 2009 03:24
16 lines
1774 bytes
1774 bytes
> My electrician says it's not an issue, but I can't see why. > > Any thoughts? > > Sylvia. Sylvia Thought one. Get rid of the electrician. In my experience with loss of neutrals it is the number one cause of electrical equipment/lighting failure. Bob AZ
Re: Two phases to house - loss of neutral
Author: F Murtz
Date: Tue, 24 Nov 2009 03:46
Date: Tue, 24 Nov 2009 03:46
24 lines
2181 bytes
2181 bytes
Sylvia Else wrote: > I have to phases of power supply to my house - so three power lines, two > phases plus neutral. > > I've on occasion wondered what would happen if we lost the neutral line. > It seems to me that we'd then have the voltage between the two phases > across two sets of appliances, one set attached to one phase, and the > other set attached to the other phase, with the two sets in series as a > result of their common connection to the neutral wire. Since the two > sets are unlikely to represent equal loads, the net result would be a > large overvoltage on one set of appliances. > > My electrician says it's not an issue, but I can't see why. > > Any thoughts? > > Sylvia. not a neutral problem but. I can remember an old lady complaining that every time she turned the hot water tap the lights came on half brilliance.and sure enough they did. she had three phase and an instantaneous three phase water heater. one phase had gone and the heater caused the dead phase to be live in series with element.(the water flow closes the heater circuit)
Re: Two phases to house - loss of neutral
Author: nesesu
Date: Tue, 24 Nov 2009 04:07
Date: Tue, 24 Nov 2009 04:07
33 lines
2532 bytes
2532 bytes
On Nov 23, 6:36 pm, "Phil Allison" <phi...@tpg.com.au> wrote: > "Trevor Wilson" > > > > > **AFAIK, the US system is fundamentally different to ours. > > ** In the US and Canada - it is NOT permitted to link neutral and earth > or plumbing within a premises. > > See here under the heading "Regulations". > > http://en.wikipedia.org/wiki/Earthing_system > > The MEN system used here in Australia seems to be unique. > > See last para on same page. > > ..... Phil Rubbish. In most of Canada, it is manditory that the neutral be bonded to earth at only ONE point, the service entrance switch enclosure. From that point an earth conductor is connected to 2 ground rods and to any metallic piping system(s). Neutral failure is a not uncommon problem especially with overhead aluminum 'triplex' service drops. A seagull deficates on the bare aluminum neutral and it soon rots off leaving an open neutral condition. Ground rod to earth resistances of 5 ohms are not uncommon, so a 10A unbalance between 'phases' could give a 50V offset of the neutral. Neil S.
Re: Two phases to house - loss of neutral
Author: nesesu
Date: Tue, 24 Nov 2009 04:13
Date: Tue, 24 Nov 2009 04:13
31 lines
2812 bytes
2812 bytes
On Nov 23, 6:40 pm, "Phil Allison" <phi...@tpg.com.au> wrote: > "kreed" > > > From what I can gather, pretty much every home in the US has a 120v - > > 0 - 120v system where the 2x 120v's are 180 degrees out of phase. > > Between the 2 phases 240v is available for stoves, air conditioners > > etc. > > > In Australia, most separate homes have a straight single phase 240v > > supply, its not common for there to be 2,3 separate phases to the > > average house. Therefore the scenario Sylvia mentions is less likely > > to occur, as not many people have this multi phase system. > > > The exception here could be blocks of flats, if the main neutral to > > the building fails, and there isn't a good earth, the imbalance could > > be a risk. > > ** There is always a good "earth" available - courtesy of the water mains > in the street being linked to neutral at every premises. > > ..... Phil All new construction [last 30 years] around here uses iron mains with rubber sealed joints and plastic service pipe into all homes, so there is NO bond from the house to the main. The Gas main is plastic, as are the service drops. So, the only earth connection is the rather 'iffy' pair of 8' ground rods usually in the rain shadow of the roof overhang. Neil S.
Re: Two phases to house - loss of neutral
Author: terryc
Date: Tue, 24 Nov 2009 04:25
Date: Tue, 24 Nov 2009 04:25
21 lines
2074 bytes
2074 bytes
On Tue, 24 Nov 2009 11:10:26 +1100, Sylvia Else wrote: > the net result would be a > large overvoltage on one set of appliances. It would be across both sets, but...... > > My electrician says it's not an issue, but I can't see why. The neutral is actually grounded to the earth for such a case; hence MEN (Multiple Earth Neutral), so the neutral would actually travel through the ground to your neighbours earth stake and back into the neutral phase there. If the USA Godzilla remake is to be believed, all your earth worms will come to the surface as an indicator, (or is that only for correct DC connections?). If you are worried about such an event happening, dump a bucket of wter on your earth stake quarterly and encourage your neighbours to do the same.
Re: Two phases to house - loss of neutral
Author: kreed
Date: Tue, 24 Nov 2009 06:49
Date: Tue, 24 Nov 2009 06:49
37 lines
2988 bytes
2988 bytes
On Nov 24, 12:40 pm, "Phil Allison" <phi...@tpg.com.au> wrote: > "kreed" > > > From what I can gather, pretty much every home in the US has a 120v - > > 0 - 120v system where the 2x 120v's are 180 degrees out of phase. > > Between the 2 phases 240v is available for stoves, air conditioners > > etc. > > > In Australia, most separate homes have a straight single phase 240v > > supply, its not common for there to be 2,3 separate phases to the > > average house. Therefore the scenario Sylvia mentions is less likely > > to occur, as not many people have this multi phase system. > > > The exception here could be blocks of flats, if the main neutral to > > the building fails, and there isn't a good earth, the imbalance could > > be a risk. > > ** There is always a good "earth" available - courtesy of the water mains > in the street being linked to neutral at every premises. > > ..... Phil That is true in a lot of cases, however I have noticed with a lot of newer houses, (in QLD anyway) they are using some kind of either black or grey pvc or poly pipe for home water mains. To make it worse, it looks to me to be "crimped" together at joins, sometimes with what look like soft metal rings but not always. Copper or the old cast iron pipes would provide an excellent Earth, and excellent soil electrical contact due to the enormous surface area of the water main in contact with the soil over distance Mine is all copper, all the way back to the water main, so no problems here.
Re: Two phases to house - loss of neutral
Author: Jasen Betts
Date: Tue, 24 Nov 2009 09:21
Date: Tue, 24 Nov 2009 09:21
20 lines
2382 bytes
2382 bytes
On 2009-11-24, Sylvia Else <sylvia@not.at.this.address> wrote: > Phil Allison wrote: >> In Australia, AC power delivery uses a system called " Multiple Earth >> Neutral " - which requires that the neutral conductors in a premises be >> connected to the plumbing system at the distribution board (ie power box). >> It also requires that an earth stake be installed for the same purpose, but >> some older premises may not have this. > > If as you say, neutral has to be tied to Earth at the premises, then I > can indeed see that the situation might not be so bad. > > On the face of it, having significant current flowing from neutral to > Earth would have to indicate a fault. It would be nice for the breakers > to trip in such a situation, but I can't see that they will. Having the breakers trip because a faulty neutral in an neighbours house (which would cause his neutral current to flow through his earth and your earth (etc) to the common neutral) could be an annoyance. bye.
Re: Two phases to house - loss of neutral
Author: Trevor Wilson
Date: Tue, 24 Nov 2009 09:36
Date: Tue, 24 Nov 2009 09:36
38 lines
2719 bytes
2719 bytes
kreed wrote: > On Nov 24, 12:40 pm, "Phil Allison" <phi...@tpg.com.au> wrote: >> "kreed" >> >>> From what I can gather, pretty much every home in the US has a 120v >>> - 0 - 120v system where the 2x 120v's are 180 degrees out of phase. >>> Between the 2 phases 240v is available for stoves, air conditioners >>> etc. >> >>> In Australia, most separate homes have a straight single phase 240v >>> supply, its not common for there to be 2,3 separate phases to the >>> average house. Therefore the scenario Sylvia mentions is less >>> likely to occur, as not many people have this multi phase system. >> >>> The exception here could be blocks of flats, if the main neutral to >>> the building fails, and there isn't a good earth, the imbalance >>> could be a risk. >> >> ** There is always a good "earth" available - courtesy of the >> water mains in the street being linked to neutral at every premises. >> >> ..... Phil > > > That is true in a lot of cases, however I have noticed with a lot of > newer houses, (in QLD anyway) they are using some kind of either black > or grey pvc or poly pipe for home water mains. To make it worse, it > looks to me to be "crimped" together at joins, sometimes with what > look like soft metal rings but not always. > **It's going to be a lot more popular too. The stuff is around half the price of copper pipes, is very easy to handle and use. -- Trevor Wilson www.rageaudio.com.au
Re: Two phases to house - loss of neutral
Author: David
Date: Tue, 24 Nov 2009 13:13
Date: Tue, 24 Nov 2009 13:13
18 lines
1866 bytes
1866 bytes
Phil Allison wrote: > > The MEN system: > > In Australia, AC power delivery uses a system called " Multiple Earth > Neutral " - which requires that the neutral conductors in a premises be > connected to the plumbing system at the distribution board (ie power box). > It also requires that an earth stake be installed for the same purpose, but > some older premises may not have this. Actually, the Neutral conductors are *NOT* connected to the plumbing system. The Neutral conductor is connected by the MEN link to the main earthing conductor, which is connected to the appropriate earth electrode. AS/NZS 3000 then requires that conductive pipe work be equipotentially bonded to the main earth conductor or earth terminal or bar (NOT to the neutral). David
Re: Two phases to house - loss of neutral
Author: Jerry Peters
Date: Tue, 24 Nov 2009 20:35
Date: Tue, 24 Nov 2009 20:35
80 lines
4836 bytes
4836 bytes
In sci.electronics.repair kreed <kenreed1999@gmail.com> wrote: > On Nov 24, 10:10 am, Sylvia Else <syl...@not.at.this.address> wrote: >> I have to phases of power supply to my house - so three power lines, two >> phases plus neutral. >> >> I've on occasion wondered what would happen if we lost the neutral line. >> It seems to me that we'd then have the voltage between the two phases >> across two sets of appliances, one set attached to one phase, and the >> other set attached to the other phase, with the two sets in series as a >> result of their common connection to the neutral wire. Since the two >> sets are unlikely to represent equal loads, the net result would be a >> large overvoltage on one set of appliances. >> >> My electrician says it's not an issue, but I can't see why. >> >> Any thoughts? >> >> Sylvia. > > > You are both right and wrong as in the absence of Neutral line, a lot > of the neutral current (imbalance) would probably flow via your earth > stake back to the transformer neutral or to a neighbours neutral via > their earth stake and while its not a perfect situation, imbalance > probably would not be as bad as you might think ? > > Of course, if there is a long run through earth (terra firma) back to > the nearest neutral, the soil is really dry, the earth stake is sub- > standard etc etc it might not work very well. > > > > > > Years and years back I once saw the result of this at a 3 phase > installation at a carnival, we were called out to fix > > They would have with them, and take from site to site portable fuse > boxes with a 3 phase plug, going to a box with breakers feeding rows > of power points going to each phase (like in a normal building > installation, but portable). They would plug in all their gear to > these sockets, and plug the 3 phase into the 3 phase sockets provided > at the venues. > > Of course, a lot of the carnival workers would probably just plug > things in at random, and who knows what load would be on the end of > each lead. There could also be very large numbers of flashing lights > on one lead too, so the load would be less than perfect, and surely > not anywhere near balanced or stable ;) > > One case, the neutral lead broke off. On one phase there was a lot of > damage to computer gear / arcade games (same sort of thing - > switchmode power supplies) etc. Some was just blown fuses, some > worse. > Note, they didn't have the earth and neutral bonded inside the box, > and didn't have a separate earth stake, where in a home fuse box they > would. > > 2 phase situation like yours would be a similar result, unless the > load was really well balanced, and consisting of mostly NON-switchmode > power supply type devices. The phase with the lowest load would > suffer overvoltage. > > This load imbalance and voltage difference would change all the time > as various appliances automatically switch off and on, like fridges, > air cons, electric HWS etc. Light bulbs may blow from overvoltage, > this would also change the balance > > > > Try connecting 12v bulbs of different wattages in series across 24v > and see what happens. The voltage will not be the same across each. > Much the same thing. I actually had the neutral fail (break) a few years back during a winter wind-storm. No deleterious effects. The imbalance (neutral) current was carried by the ground, a copper water pipe that's probably at least 10 feet below gound level and 20 0r so feet long. Jerry
Re: Two phases to house - loss of neutral
Author: Baron
Date: Tue, 24 Nov 2009 22:26
Date: Tue, 24 Nov 2009 22:26
32 lines
3058 bytes
3058 bytes
Phil Allison wrote:
>
> "kreed"
>
>> From what I can gather, pretty much every home in the US has a 120v -
>> 0 - 120v system where the 2x 120v's are 180 degrees out of phase.
>> Between the 2 phases 240v is available for stoves, air conditioners
>> etc.
>>
>> In Australia, most separate homes have a straight single phase 240v
>> supply, its not common for there to be 2,3 separate phases to the
>> average house. Therefore the scenario Sylvia mentions is less likely
>> to occur, as not many people have this multi phase system.
>>
>> The exception here could be blocks of flats, if the main neutral to
>> the building fails, and there isn't a good earth, the imbalance could
>> be a risk.
>
>
> ** There is always a good "earth" available - courtesy of the water
> mains in the street being linked to neutral at every premises.
>
>
> ..... Phil
Except where plastic is in use. Mine is all plastic and the safety
earth is linked to the armouring on the incoming mains feed cable.
--
Best Regards:
Baron.
Re: Two phases to house - loss of neutral
Author: Baron
Date: Tue, 24 Nov 2009 22:36
Date: Tue, 24 Nov 2009 22:36
32 lines
2990 bytes
2990 bytes
Meat Plow wrote:
> On Tue, 24 Nov 2009 11:10:26 +1100, Sylvia Else
> <sylvia@not.at.this.address>wrote:
>
>>I have to phases of power supply to my house - so three power lines,
>>two phases plus neutral.
>>
>>I've on occasion wondered what would happen if we lost the neutral
>>line. It seems to me that we'd then have the voltage between the two
>>phases across two sets of appliances, one set attached to one phase,
>>and the other set attached to the other phase, with the two sets in
>>series as a result of their common connection to the neutral wire.
>>Since the two sets are unlikely to represent equal loads, the net
>>result would be a large overvoltage on one set of appliances.
>>
>>My electrician says it's not an issue, but I can't see why.
>>
>>Any thoughts?
>>
>>Sylvia.
>
> Removing the return leg isn't going to cause problems in a properly
> wired US home. Don't know about the UK.
The lights would go out ! Domestic properties usually have just a 240v
single phase feed. Usually you would get a single phase running down
one side of the street and another phase running down the other.
--
Best Regards:
Baron.
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Tue, 24 Nov 2009 23:18
Date: Tue, 24 Nov 2009 23:18
30 lines
1682 bytes
1682 bytes
"David the PEDANTIC TWAT FROM HELL "
> Actually, the Neutral conductors are *NOT* connected to the plumbing
> system.
** Wot INSANE CRAPOLOGY !!
> The Neutral conductor is connected by the MEN link to the main earthing
> conductor, which is connected to the appropriate earth electrode.
** Da knee bone's connected to da thigh bone ....
> AS/NZS 3000 then requires that conductive pipe work be equipotentially
> bonded to the main earth conductor or earth terminal or bar (NOT to the
> neutral).
** Folks - you have to forgive David cos he is mentally defective.
Bad genes from his mother and his father.
Congenital autism is a curse....
..... Phil
Re: Two phases to house - loss of neutral
Author: terryc
Date: Wed, 25 Nov 2009 00:10
Date: Wed, 25 Nov 2009 00:10
9 lines
1839 bytes
1839 bytes
On Tue, 24 Nov 2009 13:40:46 +1100, Phil Allison wrote: > > ** There is always a good "earth" available - courtesy of the water > mains in the street being linked to neutral at every premises. Is this something new(<40 yrs) in the Standards in Australia? No plumbing link here. Just an earth stake under the box.
Re: Two phases to house - loss of neutral
Author: David Brodbeck
Date: Wed, 25 Nov 2009 04:54
Date: Wed, 25 Nov 2009 04:54
14 lines
2255 bytes
2255 bytes
kreed wrote: > You are both right and wrong as in the absence of Neutral line, a lot > of the neutral current (imbalance) would probably flow via your earth > stake back to the transformer neutral or to a neighbours neutral via > their earth stake and while its not a perfect situation, imbalance > probably would not be as bad as you might think ? > > Of course, if there is a long run through earth (terra firma) back to > the nearest neutral, the soil is really dry, the earth stake is sub- > standard etc etc it might not work very well. Sometimes, just to make things really exciting, some of the neutral current flows over alternate paths to a neighbor's house. These alternate paths can include things like cable TV shields.
Re: Two phases to house - loss of neutral
Author: David
Date: Wed, 25 Nov 2009 12:10
Date: Wed, 25 Nov 2009 12:10
31 lines
1946 bytes
1946 bytes
Phil Allison the unqualified drop out wrote: > >> Actually, the Neutral conductors are *NOT* connected to the plumbing >> system. ** Wot INSANE CRAPOLOGY !! > >> The Neutral conductor is connected by the MEN link to the main earthing >> conductor, which is connected to the appropriate earth electrode. > > ** Da knee bone's connected to da thigh bone .... But the Neutral not connected to the water pipe.... > > >> AS/NZS 3000 then requires that conductive pipe work be equipotentially >> bonded to the main earth conductor or earth terminal or bar (NOT to the >> neutral). > > This should explain it for you Phil. Not too technical. http://www.standards.org.au/downloads/080725_Electrical_Earthing_Standards_Alert.pdf David
David the PEDANTIC TWAT FROM HELL
Author: Phil Allison
Date: Wed, 25 Nov 2009 12:57
Date: Wed, 25 Nov 2009 12:57
32 lines
1866 bytes
1866 bytes
"David the PEDANTIC TWAT FROM HELL " > Actually, the Neutral conductors are *NOT* connected to the plumbing > system. ** Wot INSANE CRAPOLOGY !! > The Neutral conductor is connected by the MEN link to the main earthing > conductor, which is connected to the appropriate earth electrode. ** Da knee bone's connected to da thigh bone .... > AS/NZS 3000 then requires that conductive pipe work be equipotentially > bonded to the main earth conductor or earth terminal or bar (NOT to the > neutral). ** Folks - you have to forgive David cos he is mentally defective. Bad genes from his mother and his father. Congenital autism is a curse. This dude is is TOTALLY FUCKED WITH IT. ..... Phil
Re: Two phases to house - loss of neutral
Author: whit3rd
Date: Wed, 25 Nov 2009 20:10
Date: Wed, 25 Nov 2009 20:10
14 lines
2010 bytes
2010 bytes
On Nov 24, 7:54 am, Meat Plow <m...@petitmorte.net> wrote: > Removing the return leg isn't going to cause problems in a properly > wired US home. Don't know about the UK. That's just false. A properly wired US home without a neutral wire to the transformer has 240V across both phases, which can leave either phase anywhere from zero to 240 VAC. Damage to 120V appliances will result unless the breakers trip first. The 'ground' connection would have to carry the whole house's current imbalance load in place of that neutral, through the earth to some nearby dwelling that DOES have a proper neutral wire, to the same pole-pig transformer, for this calamity not to occur.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Thu, 26 Nov 2009 04:14
Date: Thu, 26 Nov 2009 04:14
6 lines
1349 bytes
1349 bytes
Leaving the neutral failure issue aside, what would happen if I disabled the Earth leakage detectors and drew power across the two phases. Would the two utility meters correctly reflect the energy I consumed? Sylvia.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Thu, 26 Nov 2009 04:23
Date: Thu, 26 Nov 2009 04:23
12 lines
1534 bytes
1534 bytes
Sylvia Else wrote: > Leaving the neutral failure issue aside, what would happen if I disabled > the Earth leakage detectors and drew power across the two phases. > > Would the two utility meters correctly reflect the energy I consumed? > > Sylvia. On second thoughts, it's pretty obvious that they wouldn't be correct, and that I'd be significantly overcharged for the power. Sylvia.
Re: Two phases to house - loss of neutral
Author: Thomas Tornblom
Date: Thu, 26 Nov 2009 07:26
Date: Thu, 26 Nov 2009 07:26
24 lines
1858 bytes
1858 bytes
Sylvia Else <sylvia@not.at.this.address> writes: > Sylvia Else wrote: >> Leaving the neutral failure issue aside, what would happen if I >> disabled the Earth leakage detectors and drew power across the two >> phases. >> Would the two utility meters correctly reflect the energy I consumed? yes. >> Sylvia. > > On second thoughts, it's pretty obvious that they wouldn't be correct, > and that I'd be significantly overcharged for the power. > > Sylvia. No you wouldn't. Each of the meters will indicate what you draw from the phases, and as you now have a higher voltage, you will also draw more power, which is what you are paying for. Thomas
Re: Two phases to house - loss of neutral
Author: Trevor Wilson
Date: Thu, 26 Nov 2009 09:57
Date: Thu, 26 Nov 2009 09:57
18 lines
1442 bytes
1442 bytes
"Sylvia Else" <sylvia@not.at.this.address> wrote in message news:006c3c5f$0$8071$c3e8da3@news.astraweb.com... > Leaving the neutral failure issue aside, what would happen if I disabled > the Earth leakage detectors and drew power across the two phases. **Depends on the equipment you connected. The damage might range from mild to catastrophic. > > Would the two utility meters correctly reflect the energy I consumed? **Briefly, yes. -- Trevor Wilson www.rageaudio.com.au
Re: Two phases to house - loss of neutral
Author: Phil Allison
Date: Thu, 26 Nov 2009 11:12
Date: Thu, 26 Nov 2009 11:12
26 lines
1585 bytes
1585 bytes
"Trevor Wilson" >> "Sillier than Anyone Else Alive " >> Leaving the neutral failure issue aside, what would happen if I disabled >> the Earth leakage detectors and drew power across the two phases. > > **Depends on the equipment you connected. The damage might range from mild > to catastrophic. ** TW has misread the Q. It is only about how domestic watt hour meters respond. >> Would the two utility meters correctly reflect the energy I consumed? > > **Briefly, yes. ** Indefinitely, actually. .... Phil
Re: Two phases to house - loss of neutral
Author: terryc
Date: Thu, 26 Nov 2009 15:19
Date: Thu, 26 Nov 2009 15:19
10 lines
1530 bytes
1530 bytes
On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >>> Would the two utility meters correctly reflect the energy I consumed? >> >> **Briefly, yes. > > ** Indefinitely, actually. Yep, that is how 415VAC is obtained.
Re: Two phases to house - loss of neutral
Author: Van Chocstraw
Date: Thu, 26 Nov 2009 21:46
Date: Thu, 26 Nov 2009 21:46
21 lines
2437 bytes
2437 bytes
Sylvia Else wrote: > I have to phases of power supply to my house - so three power lines, two > phases plus neutral. > > I've on occasion wondered what would happen if we lost the neutral line. > It seems to me that we'd then have the voltage between the two phases > across two sets of appliances, one set attached to one phase, and the > other set attached to the other phase, with the two sets in series as a > result of their common connection to the neutral wire. Since the two > sets are unlikely to represent equal loads, the net result would be a > large overvoltage on one set of appliances. > > My electrician says it's not an issue, but I can't see why. > > Any thoughts? > > Sylvia. With the exception of some pump motors, nothing in the house runs on 220. Even the stove splits 110 to the burners and 110 to the oven. No neutral and no 110's to anything.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Thu, 26 Nov 2009 23:33
Date: Thu, 26 Nov 2009 23:33
18 lines
1786 bytes
1786 bytes
terryc wrote: > On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: > > >>>> Would the two utility meters correctly reflect the energy I consumed? >>> **Briefly, yes. >> ** Indefinitely, actually. > > Yep, that is how 415VAC is obtained. But is it how it's metered? I haven't gone through the math, and I'd overlooked the fact that each meter sees a power factor of less than one, so I can't say now whether I think the meters would read correctly. But if there's a way of looking at the problem that makes the answer obvious, I've yet to see it. Sylvia.
Re: Two phases to house - loss of neutral
Author: who where
Date: Fri, 27 Nov 2009 00:25
Date: Fri, 27 Nov 2009 00:25
27 lines
2559 bytes
2559 bytes
On Thu, 26 Nov 2009 16:46:51 -0500, Van Chocstraw <boobooililililil@roadrunner.com> wrote: >Sylvia Else wrote: >> I have to phases of power supply to my house - so three power lines, two >> phases plus neutral. >> >> I've on occasion wondered what would happen if we lost the neutral line. >> It seems to me that we'd then have the voltage between the two phases >> across two sets of appliances, one set attached to one phase, and the >> other set attached to the other phase, with the two sets in series as a >> result of their common connection to the neutral wire. Since the two >> sets are unlikely to represent equal loads, the net result would be a >> large overvoltage on one set of appliances. >> >> My electrician says it's not an issue, but I can't see why. >> >> Any thoughts? >> >> Sylvia. > >With the exception of some pump motors, nothing in the house runs on >220. Even the stove splits 110 to the burners and 110 to the oven. No >neutral and no 110's to anything. Ummmm ... The O/P is in AUSTRALIA, where the supply is nominal 230V single phase, NOT in Merka like you presumably are.
Re: Two phases to house - loss of neutral
Author: PeterD
Date: Fri, 27 Nov 2009 01:54
Date: Fri, 27 Nov 2009 01:54
25 lines
1919 bytes
1919 bytes
On Fri, 27 Nov 2009 10:33:40 +1100, Sylvia Else <sylvia@not.at.this.address> wrote: >terryc wrote: >> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >> >> >>>>> Would the two utility meters correctly reflect the energy I consumed? >>>> **Briefly, yes. >>> ** Indefinitely, actually. >> >> Yep, that is how 415VAC is obtained. > >But is it how it's metered? > >I haven't gone through the math, and I'd overlooked the fact that each >meter sees a power factor of less than one, so I can't say now whether I >think the meters would read correctly. But if there's a way of looking >at the problem that makes the answer obvious, I've yet to see it. > >Sylvia. Do it the old fashioned way: make a test! Can't be that difficult, can it?
Re: Two phases to house - loss of neutral
Author: PeterD
Date: Fri, 27 Nov 2009 01:56
Date: Fri, 27 Nov 2009 01:56
27 lines
2090 bytes
2090 bytes
On Thu, 26 Nov 2009 16:46:51 -0500, Van Chocstraw <boobooililililil@roadrunner.com> wrote: >Sylvia Else wrote: >> I have to phases of power supply to my house - so three power lines, two >> phases plus neutral. >> >> I've on occasion wondered what would happen if we lost the neutral line. >> It seems to me that we'd then have the voltage between the two phases >> across two sets of appliances, one set attached to one phase, and the >> other set attached to the other phase, with the two sets in series as a >> result of their common connection to the neutral wire. Since the two >> sets are unlikely to represent equal loads, the net result would be a >> large overvoltage on one set of appliances. >> >> My electrician says it's not an issue, but I can't see why. >> >> Any thoughts? >> >> Sylvia. > >With the exception of some pump motors, nothing in the house runs on >220. Even the stove splits 110 to the burners and 110 to the oven. No >neutral and no 110's to anything. WHere are you located that this is true? Surely not in the US/North America.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Fri, 27 Nov 2009 02:21
Date: Fri, 27 Nov 2009 02:21
29 lines
2242 bytes
2242 bytes
PeterD wrote: > On Fri, 27 Nov 2009 10:33:40 +1100, Sylvia Else > <sylvia@not.at.this.address> wrote: > >> terryc wrote: >>> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >>> >>> >>>>>> Would the two utility meters correctly reflect the energy I consumed? >>>>> **Briefly, yes. >>>> ** Indefinitely, actually. >>> Yep, that is how 415VAC is obtained. >> But is it how it's metered? >> >> I haven't gone through the math, and I'd overlooked the fact that each >> meter sees a power factor of less than one, so I can't say now whether I >> think the meters would read correctly. But if there's a way of looking >> at the problem that makes the answer obvious, I've yet to see it. >> >> Sylvia. > > > Do it the old fashioned way: make a test! Can't be that difficult, can > it? Of course not. I'll just get out the 415VAC resistive load I happen to have lying around, and see what registers. Sylvia.
Re: Two phases to house - loss of neutral
Author: kreed
Date: Fri, 27 Nov 2009 07:24
Date: Fri, 27 Nov 2009 07:24
43 lines
2966 bytes
2966 bytes
On Nov 27, 7:46 am, Van Chocstraw <boobooililili...@roadrunner.com> wrote: > Sylvia Else wrote: > > I have to phases of power supply to my house - so three power lines, two > > phases plus neutral. > > > I've on occasion wondered what would happen if we lost the neutral line. > > It seems to me that we'd then have the voltage between the two phases > > across two sets of appliances, one set attached to one phase, and the > > other set attached to the other phase, with the two sets in series as a > > result of their common connection to the neutral wire. Since the two > > sets are unlikely to represent equal loads, the net result would be a > > large overvoltage on one set of appliances. > > > My electrician says it's not an issue, but I can't see why. > > > Any thoughts? > > > Sylvia. > > With the exception of some pump motors, nothing in the house runs on > 220. Even the stove splits 110 to the burners and 110 to the oven. No > neutral and no 110's to anything. Different system, there is no 110 here, only 240v and 415v As for Sylvia, yes you would be charged for the consumption. this situation would work similarly to a 3 phase delta type load The load, even unbalanced as it is, would be a certain VA at 415v - across the 2 phases How the meter responds to power factor of the load in question would be the only thing that may or may not register less KWH than actually used, but this should be to the same degree as the same load in a single phase install. IF this wasn't the case, we would have big problems regarding billing on installs having both single and 3 phase loads on the same meters in 3 phase premises.
Re: Two phases to house - loss of neutral
Author: F Murtz
Date: Fri, 27 Nov 2009 08:53
Date: Fri, 27 Nov 2009 08:53
33 lines
2573 bytes
2573 bytes
Sylvia Else wrote: > PeterD wrote: >> On Fri, 27 Nov 2009 10:33:40 +1100, Sylvia Else >> <sylvia@not.at.this.address> wrote: >> >>> terryc wrote: >>>> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >>>> >>>> >>>>>>> Would the two utility meters correctly reflect the energy I >>>>>>> consumed? >>>>>> **Briefly, yes. >>>>> ** Indefinitely, actually. >>>> Yep, that is how 415VAC is obtained. >>> But is it how it's metered? >>> >>> I haven't gone through the math, and I'd overlooked the fact that >>> each meter sees a power factor of less than one, so I can't say now >>> whether I think the meters would read correctly. But if there's a way >>> of looking at the problem that makes the answer obvious, I've yet to >>> see it. >>> >>> Sylvia. >> >> >> Do it the old fashioned way: make a test! Can't be that difficult, can >> it? > > Of course not. I'll just get out the 415VAC resistive load I happen to > have lying around, and see what registers. > > Sylvia. Two large lamps in series.
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Fri, 27 Nov 2009 11:31
Date: Fri, 27 Nov 2009 11:31
42 lines
2643 bytes
2643 bytes
F Murtz wrote: > Sylvia Else wrote: >> PeterD wrote: >>> On Fri, 27 Nov 2009 10:33:40 +1100, Sylvia Else >>> <sylvia@not.at.this.address> wrote: >>> >>>> terryc wrote: >>>>> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >>>>> >>>>> >>>>>>>> Would the two utility meters correctly reflect the energy I >>>>>>>> consumed? >>>>>>> **Briefly, yes. >>>>>> ** Indefinitely, actually. >>>>> Yep, that is how 415VAC is obtained. >>>> But is it how it's metered? >>>> >>>> I haven't gone through the math, and I'd overlooked the fact that >>>> each meter sees a power factor of less than one, so I can't say now >>>> whether I think the meters would read correctly. But if there's a way >>>> of looking at the problem that makes the answer obvious, I've yet to >>>> see it. >>>> >>>> Sylvia. >>> >>> >>> Do it the old fashioned way: make a test! Can't be that difficult, can >>> it? >> >> Of course not. I'll just get out the 415VAC resistive load I happen to >> have lying around, and see what registers. >> >> Sylvia. > Two large lamps in series. > I don't have any. I'd have to buy them. Anyway, all a test would do is show that the answer is probably correct. It wouldn't make it any more obvious. Sylvia.
Re: Two phases to house - loss of neutral
Author: PeterD
Date: Fri, 27 Nov 2009 14:13
Date: Fri, 27 Nov 2009 14:13
35 lines
2438 bytes
2438 bytes
On Fri, 27 Nov 2009 13:21:08 +1100, Sylvia Else <sylvia@not.at.this.address> wrote: >PeterD wrote: >> On Fri, 27 Nov 2009 10:33:40 +1100, Sylvia Else >> <sylvia@not.at.this.address> wrote: >> >>> terryc wrote: >>>> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote: >>>> >>>> >>>>>>> Would the two utility meters correctly reflect the energy I consumed? >>>>>> **Briefly, yes. >>>>> ** Indefinitely, actually. >>>> Yep, that is how 415VAC is obtained. >>> But is it how it's metered? >>> >>> I haven't gone through the math, and I'd overlooked the fact that each >>> meter sees a power factor of less than one, so I can't say now whether I >>> think the meters would read correctly. But if there's a way of looking >>> at the problem that makes the answer obvious, I've yet to see it. >>> >>> Sylvia. >> >> >> Do it the old fashioned way: make a test! Can't be that difficult, can >> it? > >Of course not. I'll just get out the 415VAC resistive load I happen to >have lying around, and see what registers. > >Sylvia. If you can't find it, you can borrow mine... Oh, wait, too far away! <bg> Couple of (identical) resistance electric heaters, in series?
Re: Two phases to house - loss of neutral
Author: baron
Date: Fri, 27 Nov 2009 15:57
Date: Fri, 27 Nov 2009 15:57
28 lines
2547 bytes
2547 bytes
Sylvia Else Inscribed thus:
> terryc wrote:
>> On Thu, 26 Nov 2009 22:12:24 +1100, Phil Allison wrote:
>>
>>
>>>>> Would the two utility meters correctly reflect the energy I
>>>>> consumed?
>>>> **Briefly, yes.
>>> ** Indefinitely, actually.
>>
>> Yep, that is how 415VAC is obtained.
>
> But is it how it's metered?
>
> I haven't gone through the math, and I'd overlooked the fact that each
> meter sees a power factor of less than one, so I can't say now whether
> I think the meters would read correctly. But if there's a way of
> looking at the problem that makes the answer obvious, I've yet to see
> it.
>
> Sylvia.
I have three meters, one for each phase.
--
Best Regards:
Baron.
Re: Two phases to house - loss of neutral
Author: David
Date: Sat, 28 Nov 2009 00:28
Date: Sat, 28 Nov 2009 00:28
29 lines
2376 bytes
2376 bytes
Sylvia Else wrote: > > Anyway, all a test would do is show that the answer is probably correct. > It wouldn't make it any more obvious. > > Sylvia. Sylvia, Draw yourself a vector diagram. Then with some simple trigonometry it *should* be more obvious. Assume a resistive load between two of the three phases, with a load of 1 unit current and 1 unit voltage. The load will thus be 1 unit power. Each single phase meter will see the in phase voltage as 1 / sqrt(3) (240/415). Each single phase meter will see an in phase current of 1 x cos(30). Remember that cos(30) = 1/2 sqrt(3). This gives the power measured by each meter as V*I = 1/sqrt(3) * 1/2 sqrt(3) The two square roots of three cancel, which, unsurprisingly leaves 1/2. Thus each meter records 1/2 the power in the load, and you will thus get billed correctly. David
Re: Two phases to house - loss of neutral
Author: Sylvia Else
Date: Sat, 28 Nov 2009 00:36
Date: Sat, 28 Nov 2009 00:36
21 lines
2045 bytes
2045 bytes
David wrote: > Sylvia Else wrote: >> >> Anyway, all a test would do is show that the answer is probably >> correct. It wouldn't make it any more obvious. >> >> Sylvia. > > Sylvia, > > Draw yourself a vector diagram. Then with some simple trigonometry it > *should* be more obvious. <sigh> The test wouldn't make it more obvious. I said I hadn't done the math. The math would give the result, not make it obvious. Sylvia.