Thread View: uk.comp.homebuilt
14 messages
14 total messages
Started by Paul Hopwood
Mon, 07 Jun 2004 22:19
APC SmartUPS problem
Author: Paul Hopwood
Date: Mon, 07 Jun 2004 22:19
Date: Mon, 07 Jun 2004 22:19
20 lines
1834 bytes
1834 bytes
I'm running a PC off a APC SmartUPS 420. It passes self-test and, after four hours or so, the PowerChute software reports the battery capacity to be at 100% with 6 minutes of runtime remaining. The load looks fine, with one PC fitted with a 400W PSU drawing around 35%-40% of capacity, depending on what it's doing at the time. However, if I pull the AC supply the UPS and the attached server die immediately. If I run PowerChute after reconnecting power and bringing it back up it reports the battery is discharged and only has about 20% charge with less than a minute run time. My gut feeling is the battery is shafted (if so any recommendations where I can buy a replacement without paying APC reseller prices?) but I'm not entirely convinced as it behaves as I'd expect a good one to, shows normal charging patterns and passes the UPS self-test. Anyone able to shed any light on it? -- >iv< Paul >iv<
Re: APC SmartUPS problem
Author: nevje
Date: Mon, 07 Jun 2004 22:51
Date: Mon, 07 Jun 2004 22:51
9 lines
1176 bytes
1176 bytes
> My gut feeling is the battery is shafted (if so any recommendations > where I can buy a replacement without paying APC reseller prices?) but > I'm not entirely convinced as it behaves as I'd expect a good one to, > shows normal charging patterns and passes the UPS self-test. Anyone > able to shed any light on it? > > http://www.psaparts.co.uk
Re: APC SmartUPS problem
Author: Alex Threlfall
Date: Tue, 08 Jun 2004 10:46
Date: Tue, 08 Jun 2004 10:46
30 lines
2294 bytes
2294 bytes
In article <jfq9c01kogmrku8hedjt5hrb4k4e8ea1pj@4ax.com>, paul@hopwood.org.uk says... > > I'm running a PC off a APC SmartUPS 420. It passes self-test and, > after four hours or so, the PowerChute software reports the battery > capacity to be at 100% with 6 minutes of runtime remaining. The load > looks fine, with one PC fitted with a 400W PSU drawing around 35%-40% > of capacity, depending on what it's doing at the time. > > However, if I pull the AC supply the UPS and the attached server die > immediately. If I run PowerChute after reconnecting power and > bringing it back up it reports the battery is discharged and only has > about 20% charge with less than a minute run time. > > My gut feeling is the battery is shafted (if so any recommendations > where I can buy a replacement without paying APC reseller prices?) but > I'm not entirely convinced as it behaves as I'd expect a good one to, > shows normal charging patterns and passes the UPS self-test. Anyone > able to shed any light on it? > > RS Components, the batteries are probably shafted as you say. I fixed mine by getting new batteries for it, and it's been running for the last year just fine ;) -- Alex Threlfall Cyberprog New Media www.cyberprog.net tel - 0870 446 0789 fax - 0870 446 1789
Re: APC SmartUPS problem
Author: Dorothy Bradbury
Date: Tue, 08 Jun 2004 11:19
Date: Tue, 08 Jun 2004 11:19
13 lines
1729 bytes
1729 bytes
Check around on batteries carefully, sometimes Alarm people can do or get the right size at better prices than typical component suppliers. That was true of the 11Ah size used on SmartUPS1000, may also be true of the 420 - but yes, your batteries are defective. That said, if you want to be sure, find an alarm installer and ask if they can put your batteries on their lead-acid capacity tester. They are expensive LCD capacity assessors (the units, not the people :-) -- Dorothy Bradbury www.stores.ebay.co.uk/panaflofan for fans, books & other items http://homepage.ntlworld.com/dorothy.bradbury/panaflo.htm (Direct)
Re: APC SmartUPS problem
Author: Clint Sharp
Date: Tue, 08 Jun 2004 14:30
Date: Tue, 08 Jun 2004 14:30
21 lines
1980 bytes
1980 bytes
In message <jfq9c01kogmrku8hedjt5hrb4k4e8ea1pj@4ax.com>, Paul Hopwood <paul@hopwood.org.uk> writes > >I'm running a PC off a APC SmartUPS 420. It passes self-test and, >after four hours or so, the PowerChute software reports the battery >capacity to be at 100% with 6 minutes of runtime remaining. The load >looks fine, with one PC fitted with a 400W PSU drawing around 35%-40% >of capacity, depending on what it's doing at the time. > >However, if I pull the AC supply the UPS and the attached server die >immediately. If I run PowerChute after reconnecting power and >bringing it back up it reports the battery is discharged and only has >about 20% charge with less than a minute run time. > >My gut feeling is the battery is shafted Go with your gut. RS components, Farnell, CPC or (shudder) Maplin should all be able to supply. To test the battery, you could stick a car headlight bulb across it and monitor the battery voltage, I bet it would drop off real quick. -- Clint Sharp
Re: APC SmartUPS problem
Author: Paul Hopwood
Date: Tue, 08 Jun 2004 17:54
Date: Tue, 08 Jun 2004 17:54
21 lines
1858 bytes
1858 bytes
Alex Threlfall <alex@nospam.cyberprog.net> wrote: >> My gut feeling is the battery is shafted (if so any recommendations >> where I can buy a replacement without paying APC reseller prices?) but >> I'm not entirely convinced as it behaves as I'd expect a good one to, >> shows normal charging patterns and passes the UPS self-test. Anyone >> able to shed any light on it? >RS Components, the batteries are probably shafted as you say. I fixed >mine by getting new batteries for it, and it's been running for the last >year just fine ;) Thanks all for the advice. Four out of four is good enough for me! ;-) I've got a new battery on order; Yuasa part worked out half the price of an APC replacement. Once it's delivered and fitted I'll feedback if it's fixed the problem. -- >iv< Paul >iv<
Re: APC SmartUPS problem
Author: nevje
Date: Tue, 08 Jun 2004 22:03
Date: Tue, 08 Jun 2004 22:03
12 lines
1498 bytes
1498 bytes
> Thanks all for the advice. Four out of four is good enough for me! > ;-) > > I've got a new battery on order; Yuasa part worked out half the price > of an APC replacement. Once it's delivered and fitted I'll feedback > if it's fixed the problem. ive used psa parts for batteries of all sorts - had great success for odd type laptop bios battery too - especially the 3 or 4 cell in a plastic package type - if they didnt have stock send them the part and they used to refurb them, basically remake something identical for a small fee - very useful.
Re: APC SmartUPS problem
Author: Paul Hopwood
Date: Thu, 10 Jun 2004 20:00
Date: Thu, 10 Jun 2004 20:00
17 lines
1766 bytes
1766 bytes
Paul Hopwood <paul@hopwood.org.uk> wrote: >>> My gut feeling is the battery is shafted (if so any recommendations >>> where I can buy a replacement without paying APC reseller prices?) but >>> I'm not entirely convinced as it behaves as I'd expect a good one to, >>> shows normal charging patterns and passes the UPS self-test. Anyone >>> able to shed any light on it? >I've got a new battery on order; Yuasa part worked out half the price >of an APC replacement. Once it's delivered and fitted I'll feedback >if it's fixed the problem. Battery arrived today, was fitted and appears to have fixed the problem. Thanks to everyone who offered advice. -- >iv< Paul >iv<
Re: APC SmartUPS problem
Author: Graham W
Date: Thu, 10 Jun 2004 23:22
Date: Thu, 10 Jun 2004 23:22
22 lines
2419 bytes
2419 bytes
Paul Hopwood wrote: > Paul Hopwood <paul@hopwood.org.uk> wrote: > >>>> My gut feeling is the battery is shafted (if so any recommendations >>>> where I can buy a replacement without paying APC reseller prices?) <...> >> I've got a new battery on order; Yuasa part worked out half the price >> of an APC replacement. > > Battery arrived today, was fitted and appears to have fixed the > problem. Thanks to everyone who offered advice. It would be worth checking the terminal voltage under charging conditions to make sure that the death of its predecessor wasn't down to over-charging. 13.8V is often quoted as suitable for sealed lead-acid batteries. -- Graham W http://www.gcw.org.uk/ PGM-FI page updated, Graphics Tutorial WIMBORNE http://www.wessex-astro-society.freeserve.co.uk/ Wessex Dorset UK Astro Society's Web pages, Info, Meeting Dates, Sites & Maps Change 'news' to 'sewn' in my Reply address to avoid my spam filter.
Re: APC SmartUPS problem
Author: Paul Hopwood
Date: Fri, 11 Jun 2004 23:19
Date: Fri, 11 Jun 2004 23:19
21 lines
2035 bytes
2035 bytes
"Graham W" <graham@his.com.puter.INVALID> wrote: >>> I've got a new battery on order; Yuasa part worked out half the price >>> of an APC replacement. >> Battery arrived today, was fitted and appears to have fixed the >> problem. Thanks to everyone who offered advice. >It would be worth checking the terminal voltage under charging >conditions to make sure that the death of its predecessor wasn't >down to over-charging. 13.8V is often quoted as suitable for >sealed lead-acid batteries. According to the PowerChute software the UPS itself reports the voltage at 13.85V. Any reason I should mistrust it? The UPS was manufactured in 1999 and, to the best of my knowledge, was still on the original battery so probably just died of old age. :) -- >iv< Paul >iv<
Re: APC SmartUPS problem
Author: Graham W
Date: Sat, 12 Jun 2004 03:09
Date: Sat, 12 Jun 2004 03:09
39 lines
2810 bytes
2810 bytes
"Paul Hopwood" <paul@hopwood.org.uk> wrote in message news:4bfkc0tp79ta5cir8nvtjas5hejp6961md@4ax.com... > "Graham W" <graham@his.com.puter.INVALID> wrote: > > >>> I've got a new battery on order; Yuasa part worked out half the price > >>> of an APC replacement. > > >> Battery arrived today, was fitted and appears to have fixed the > >> problem. Thanks to everyone who offered advice. > > >It would be worth checking the terminal voltage under charging > >conditions to make sure that the death of its predecessor wasn't > >down to over-charging. 13.8V is often quoted as suitable for > >sealed lead-acid batteries. > > According to the PowerChute software the UPS itself reports the > voltage at 13.85V. That's fine. > Any reason I should mistrust it? No. > The UPS was manufactured in 1999 and, to the best of my knowledge, was > still on the original battery so probably just died of old age. :) If on the other hand, the voltage was 14.2V there would be a suspicion of batterycide (is that a word? 8�), which would shortly be followed the demise of the new replacement. -- Graham W http://www.gcw.org.uk/ PGM-FI page update, Graphics Tutorial WIMBORNE http://www.wessex-astro-society.freeserve.co.uk/ Wessex Dorset UK Astro Society's Web pages, Info, Meeting Dates, Sites & Maps Change 'news' to 'sewn' in my Reply address to avoid my spam filter.
Re: APC SmartUPS problem
Author: jasee
Date: Sat, 12 Jun 2004 17:09
Date: Sat, 12 Jun 2004 17:09
30 lines
2468 bytes
2468 bytes
Graham W wrote: > "Paul Hopwood" <paul@hopwood.org.uk> wrote in message > news:4bfkc0tp79ta5cir8nvtjas5hejp6961md@4ax.com... >> "Graham W" <graham@his.com.puter.INVALID> wrote: >>> It would be worth checking the terminal voltage under charging >>> conditions to make sure that the death of its predecessor wasn't >>> down to over-charging. 13.8V is often quoted as suitable for >>> sealed lead-acid batteries. >> >> According to the PowerChute software the UPS itself reports the >> voltage at 13.85V. > If on the other hand, the voltage was 14.2V there would be a suspicion > of batterycide (is that a word? 8�), which would shortly be followed > the demise of the new replacement. I'm not sure about this, provided the maximum current isn't succeeded then I don't think there is a problem, for instance I've often revived sealed lead acid batteries by putting the voltage up (with a variable supply) until it starts drawing current then reduced it as it rises to about a tenth of its rated current. This can revive dead batteries. Sometimes I have to wack the voltage up to 20 volts or more, before the current increases. I think overheating (which is fatal) is caused by too great a current (when charging). --- Outgoing mail is certified Virus Free. Checked by AVG anti-virus system (http://www.grisoft.com). Version: 6.0.676 / Virus Database: 438 - Release Date: 5/3/04
Re: APC SmartUPS problem
Author: Dr John Stockton
Date: Sat, 12 Jun 2004 18:44
Date: Sat, 12 Jun 2004 18:44
26 lines
2576 bytes
2576 bytes
JRS: In article <4bfkc0tp79ta5cir8nvtjas5hejp6961md@4ax.com>, seen in news:demon.tech.pc, Paul Hopwood <paul@hopwood.org.uk> posted at Sat, 12 Jun 2004 00:19:45 : >"Graham W" <graham@his.com.puter.INVALID> wrote: >>It would be worth checking the terminal voltage under charging >>conditions to make sure that the death of its predecessor wasn't >>down to over-charging. 13.8V is often quoted as suitable for >>sealed lead-acid batteries. > >According to the PowerChute software the UPS itself reports the >voltage at 13.85V. Any reason I should mistrust it? Yes. You should mistrust any stated measurement that has no stated uncertainty; and, while I don't doubt the truth of what Graham actually posted, one needs to be given a range of suitability. It is not safe to presume, just because 13.8 was written, that X is satisfactory if and only if 13.75 <= X < 13.85 - although that may be the case. -- � John Stockton, Surrey, UK. ?@merlyn.demon.co.uk / ??.Stockton@physics.org � Web <URL:http://www.merlyn.demon.co.uk/> - FAQish topics, acronyms, & links. Correct <= 4-line sig. separator as above, a line precisely "-- " (SoRFC1036) Do not Mail News to me. Before a reply, quote with ">" or "> " (SoRFC1036)
Re: APC SmartUPS problem
Author: Graham W
Date: Sat, 12 Jun 2004 21:51
Date: Sat, 12 Jun 2004 21:51
39 lines
3403 bytes
3403 bytes
jasee wrote: > Graham W wrote: >> "Paul Hopwood" <paul@hopwood.org.uk> wrote in message >> news:4bfkc0tp79ta5cir8nvtjas5hejp6961md@4ax.com... >>> "Graham W" <graham@his.com.puter.INVALID> wrote: >>>> It would be worth checking the terminal voltage under charging >>>> conditions to make sure that the death of its predecessor wasn't >>>> down to over-charging. 13.8V is often quoted as suitable for >>>> sealed lead-acid batteries. >>> >>> According to the PowerChute software the UPS itself reports the >>> voltage at 13.85V. >> If on the other hand, the voltage was 14.2V there would be a >> suspicion >> of batterycide (is that a word? 8�), which would shortly be >> followed the demise of the new replacement. > > I'm not sure about this, provided the maximum current isn't succeeded > then I don't think there is a problem, for instance I've often > revived sealed lead acid batteries by putting the voltage up (with a > variable supply) until it starts drawing current then reduced it as > it rises to about a tenth of its rated current. This can revive dead > batteries. Sometimes I have to wack the voltage up to 20 volts or > more, before the current increases. I think overheating (which is > fatal) is caused by too great a current (when charging). You are not following the discussion! If you take a new battery and impose 14.2V across it (because of a faulty control unit), it will draw a lot of current and drive off the electrolyte. What we are not discussing is abusing *OLD* useless batteries to try and recover some useful service from them. -- Graham W http://www.gcw.org.uk/ PGM-FI page updated, Graphics Tutorial WIMBORNE http://www.wessex-astro-society.freeserve.co.uk/ Wessex Dorset UK Astro Society's Web pages, Info, Meeting Dates, Sites & Maps Change 'news' to 'sewn' in my Reply address to avoid my spam filter.